Help with Central Air !!!!


Please bear with me here I have no clue about Air conditioning other than you flip the switch to cool and set the temp oh yeah and close the windows.

Today the ac unit froze both the part that is outside and it seemed like inside the house it was frozen as well since no air was moving through the vents.

The AC people we called recommended changing the furnace Air filter and allowing the unit to thaw. Then restart the AC and if it happens again to call them. (they can't get anyone out until mid july though). The filter is changed and we are letting it thaw now.

Any one know what may have caused this and if there is anything we can do to prevent or correct this problem?

Thanks in Advance
Registered Members don't see these ads. Register now it's free!
__________________




Kelli
dobejazz is offline   Reply With Quote
Old 06-02-2006, 07:00 PM   #2
VWD
BIG SMELLY MOD
 
VWD's Avatar
 
Join Date: Dec 2004
Location: Livingston Parish, Denham Springs, Louisiana
Posts: 16,860
Images: 421
I agree on the filter change Kelli, When it gets plugged that will happen. Was the filter dirty, Low freon can also cuase it.
__________________


Vince aka VINNIE
VWD is offline   Reply With Quote
Old 06-02-2006, 07:48 PM   #3
Junkzoo
Look deeply into my eyes
 
Junkzoo's Avatar
 
Join Date: Aug 2001
Location: NW Indiana
Posts: 11,051
Paging RickO ,,,,paging RickO,,,,,,
He's one of our resident HVAC guys, that might be able to help,,,,,,mebbe if you PM him , and point him to this thread,,,,he might chime in,,,,
__________________
Jeff
ieSpell-Use it/learn it/live it.If you think you don't need it, you do!
http://www.iespell.com/
Junkzoo is offline   Reply With Quote
Old 06-02-2006, 07:54 PM   #4
Junkzoo
Look deeply into my eyes
 
Junkzoo's Avatar
 
Join Date: Aug 2001
Location: NW Indiana
Posts: 11,051
Kelli, i just PM'ed Rick for ya,,,,,but if/when he shows up here, i would quess the filter,,,mebbe air flow across the coils,,,,,(obstruction,dirty filter,slow/dead blower fan?)
are you letting the unit "cycle" ,,meaning the compressor turns off once inne while,,,sometimes leaving it run all the time can lead to a freeze up condition,,,at least the cranes and such at work will do that,,,,
__________________
Jeff
ieSpell-Use it/learn it/live it.If you think you don't need it, you do!
http://www.iespell.com/
Junkzoo is offline   Reply With Quote
Old 06-02-2006, 08:08 PM   #5
dobejazz
Duper Mod !
 
dobejazz's Avatar
 
Join Date: Mar 2005
Location: Illinois
Posts: 13,974
Images: 1308
Thanks Jeff We changed the filter it needed to be changed but didn't seem to bad. It's actually been cooler here the last few days But we just turned it on for the season last Friday I think I'm not sure if the compressor turns off (I'm bad I know) I assume it does at night
__________________




Kelli
dobejazz is offline   Reply With Quote
Old 06-02-2006, 08:31 PM   #6
Rick O
Good boy
 
Rick O's Avatar
 
Join Date: Jan 2000
Location: Marietta, GA, USA
Posts: 7,882
Images: 54
Wow. Mid July? And I thought I was busy.

Several things can cause an AC to freeze up. The two most common are low on freon and restricted airflow (the examples Jeff gave you). Unless your filter was stopped up then changing the filter isn't really going to solve your problem. Assuming it worked well last Summer something has gone wrong. As a homeowner about the only things you can address is restricted airflow. The ice you see is only the tip of the iceburg so to speak. The freezing up started at the evaporator coil which is (or should be) enclosed in a plenum above or beside the furnace or air handler.

The first thing to do is thaw out the coil. I would turn the heat on and turbo melt it but I only do that when I know I'm going to be able to provide the homeowner with cooling that very same day. That will add a lot of heat to the house. A safer way is the set the fan switch on the thermostat to "on" and set the "heat/cool" switch to off. Walk outside and make sure the condenser doesn't continue to run even after it's been turned off. Stuck contactors although rare does happen occasionally. That will make the condenser run even when it's turned off. If there is ice on the coil you won't feel any air coming out of the vents but check to see if you can hear the blower running at the furnace. Be prepared for a lot of water on the floor. I mean gallons. All that ice has to go somewhere and chances are the coil drain will be blocked by the ice. A shop vac or lots of towels and a bucket are handy to have close by.

After you know the ice is melted, prolly 12+ hours, we're ready to diagnose the problem. Turn the AC on and set the temp to a low enough temp so that it will stay on for a while. Check to see that the blower is operating and feel for a good air flow coming out of the vents. Make sure that all of the registers are open and that none of them are blocked by furniture. Some will be returns and will be sucking air but they need to be unobstructed too. If everything is ok at this point we're going to feel the refrigeration lines and check for cooling. You will see two refrigeration lines coming out of the evaporator coil. One will be a small (about 3/8") liquid line with no insulation on it, the other will be larger (about 7/8") suction line that should have foam insulation on it. The suction line is the one we're interested in for now. After the system has been running for 10 minutes or so pull back the foam insulation and feel the copper line. We're looking for cold and sweaty, somewhere in the neighborhood of 45-60 degrees. If you have that then good, if not then most likely it's low on freon.

This is kinda tough to do by typing so if you PM me I can give you me cell # and you can call me tomorrow and I'll walk you through it.

Good luck.
__________________
Rick O is offline   Reply With Quote
Old 06-02-2006, 08:36 PM   #7
dobejazz
Duper Mod !
 
dobejazz's Avatar
 
Join Date: Mar 2005
Location: Illinois
Posts: 13,974
Images: 1308
Thanks Rick ! We do have the fan on now with the Air/Heat off I printing this now to give my husband
__________________




Kelli
dobejazz is offline   Reply With Quote
Old 06-03-2006, 12:25 AM   #8
Junkzoo
Look deeply into my eyes
 
Junkzoo's Avatar
 
Join Date: Aug 2001
Location: NW Indiana
Posts: 11,051
Hope Rick gave you some good info , toward fixing your A/C up Kelli,,,,,
As one who can't seem to live w/out A/C,,,,i can feel for someone that has a problem with theirs
,,,,,i had a problem with my heat/air system last summer,,,,and i took care of it,,,,,i got a new one! LOL

Bring on the heat!
__________________
Jeff
ieSpell-Use it/learn it/live it.If you think you don't need it, you do!
http://www.iespell.com/

Last edited by Junkzoo; 06-03-2006 at 12:46 AM.
Junkzoo is offline   Reply With Quote
Old 06-03-2006, 01:39 AM   #9
gwen_o_lyn
Nothing to See Here
 
gwen_o_lyn's Avatar
 
Join Date: Oct 2004
Location: Cartersville, Georgia
Posts: 2,995
Rick- I may just have to call u out to my house. You give discounts to people with reef tanks, right??

The last guy out here about a month ago said our unit has a leak and recommended getting a new one. The warrenty just expired too. I know they put the cheapest crap in these new houses. The guy did something and said it would last for a little while... so I don't know.

So far everything is ok, I'm crossing my fingers though.

Kelli- hope yours is working soon!!
gwen_o_lyn is offline   Reply With Quote
Old 06-03-2006, 03:17 AM   #10
Loverotties
I've got the REEF rash!
 
Loverotties's Avatar
 
Join Date: Nov 2004
Location: New Jersey
Posts: 24,657
Hopefully just a bad filter one other problem people do is they turn the thermostat down real low thinking it will cool quicker (which it won't) and leave it there and specially over night they freeze up the coil.But Rick is the man,He typed it perfect!Hope it's OK!Kelli.
__________________
Loverotties is offline   Reply With Quote
Old 06-03-2006, 08:09 AM   #11
Minnreefer
A goof
 
Minnreefer's Avatar
 
Join Date: Jan 2000
Location: Plymouth, MN USA
Posts: 2,923
Rick or anyone else, do you have recomendations on a good ac unit, the previous owners replaced my furnace before I moved in but my ac unit is probably 25 years old, it is currently working fine, but.....

Thanks

Jon
Minnreefer is offline   Reply With Quote
Old 06-03-2006, 08:14 AM   #12
dobejazz
Duper Mod !
 
dobejazz's Avatar
 
Join Date: Mar 2005
Location: Illinois
Posts: 13,974
Images: 1308
Well we left it off overnight I just turned it on I had to turn it down some it's set to cool to 75 and currently the house is 73. I'll keep ya posted
__________________




Kelli
dobejazz is offline   Reply With Quote
Old 06-03-2006, 01:07 PM   #13
Rick O
Good boy
 
Rick O's Avatar
 
Join Date: Jan 2000
Location: Marietta, GA, USA
Posts: 7,882
Images: 54
Quote:
Originally Posted by Minnreefer
Rick or anyone else, do you have recomendations on a good ac unit, the previous owners replaced my furnace before I moved in but my ac unit is probably 25 years old, it is currently working fine, but.....

Thanks

Jon
I've never seen so many problems with new AC's as I have in the last year. I used to like Trane but I've had a rash of bad compressors on less than one year old Tranes lately.

Unless you can find one that was manufactured before January '06 you're going to have to get a 13 SEER or higher. Not that that's a bad thing but it will be more expensive.
__________________
Rick O is offline   Reply With Quote
Reply

Bookmarks



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On

Sitemap:1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185
Sponsor Our Community

All times are GMT -5. The time now is 07:23 PM.


Powered by vBulletin® Version 3.7.0
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
Our lawyer tells us that, by pressing the "New Thread" or "New Reply" button, you acknowledge that the opinions and information expressed in your article are yours alone and not those of thereeftank.com, dba The Reef Tank. Further, you agree to indemnify The Reef Tank, its moderators, administrators and agents from any and all liability which may arise as a result of your article. (C)opyright 2006 TheReefTank.com