PC Ballast and GFCI Problem


Hi All,

Has anyone ever encountered a PC ballast that would keep tripping out the GFCI? It seems that mine is everytime I plug it in. I really do not want to take out the GFCI but I cannot run the PCs with it. Does anyone have a solution?

Thanks
Registered Members don't see these ads. Register now it's free!
Pauli is offline   Reply With Quote
Old 09-08-2006, 09:18 AM   #2
Loverotties
I've got the REEF rash!
 
Loverotties's Avatar
 
Join Date: Nov 2004
Location: New Jersey
Posts: 23,089
Bad ballast,lose wire,bad GFCI outlet...etc
__________________
Loverotties is offline   Reply With Quote
Old 09-08-2006, 10:45 AM   #3
Pauli
Little Fishy
 
Pauli's Avatar
 
Join Date: May 2006
Location: Michigan
Posts: 233
The manufacturer of the lights state that the ballast might be incompatible with the GFCI. This seems alittle weird. I will check into the wires inside the ballast housing and maybe put in a different GFCI to see it it might be the cause.
Pauli is offline   Reply With Quote
Old 09-08-2006, 10:53 AM   #4
Wiskey
Just some guy, you know?
 
Wiskey's Avatar
 
Join Date: Sep 2005
Location: Phoenix AZ
Posts: 17,687
Images: 70
I have 6 PC ballasts on GFI's, along with 2 T5 ballasts, and 2 MH ballasts, none of them pop the GFI. If this ballast does I would not use it.

Just my $0.02
Whiskey
__________________
"Life is a daring adventure - Or nothing."
"Be the water, not the rock."

Kaizen
Wiskey is offline   Reply With Quote
Old 09-08-2006, 11:02 AM   #5
coralcat
Little Fishy
 
Join Date: Jun 2006
Location: NW
Posts: 203
I have doul ballast on timers with gfi, one would keep tripping, I thought it was the gfi, it wasn't, it was the ballast, one of the doul, so, check it well. ya don't need a meltdown. aND YES, gfi'S CAN AND DO GO BAD, That's another reason they have a test butin.
coralcat is offline   Reply With Quote
Old 09-08-2006, 03:59 PM   #6
Wolfenbuttel
Big Fishy
 
Wolfenbuttel's Avatar
 
Join Date: Jul 2006
Location: NY
Posts: 563
Images: 9
depending on the type of gfci the manufacurs rating is different. The gfci is bad or u r getin a "nucence trip". All that is, is current flow back on the neutral of the gfci and trippin the button. A loose wire normaly wont do it. My guess is that the ballest is bad. Try plugging in another light and see if the gfci trips. U could also try changing the outlet to a standard outlet.
Wolfenbuttel is offline   Reply With Quote
Old 09-08-2006, 04:07 PM   #7
whatevva
The Muddy Mod
 
whatevva's Avatar
 
Join Date: Dec 2005
Location: Uxbridge, MA
Posts: 4,977
Quote:
All that is, is current flow back on the neutral of the gfci and trippin the button.
Ummm... there is ALWAYS current flow on the neutral of a circuit in use. GFCI's trip on a reduction of resistance between neutral and ground or hot and ground, and NEVER hot to neutral.

Check to see if they grounded one side of the transformer to the case of the ballast. That would make neutral and ground common and trip a GFCI.
__________________
Butch
"I'm King of the Sea People" - Cartman
Member - TriState Reef Society

http://thereeftank.com/forums/showthread.php?t=76110
whatevva is offline   Reply With Quote
Old 09-08-2006, 06:41 PM   #8
Loverotties
I've got the REEF rash!
 
Loverotties's Avatar
 
Join Date: Nov 2004
Location: New Jersey
Posts: 23,089
Hope you find it.
__________________
Loverotties is offline   Reply With Quote
Old 09-09-2006, 11:59 AM   #9
Pauli
Little Fishy
 
Pauli's Avatar
 
Join Date: May 2006
Location: Michigan
Posts: 233
It is still weird. There are two ballasts in the housing and each of them trip 3 different GFCIs. I have rma'd the ballasts. The manufacturer says that they are going to replace it. Now, ten days without PC. Good thing I have the mh.
Pauli is offline   Reply With Quote
Old 09-10-2006, 06:54 AM   #10
Wolfenbuttel
Big Fishy
 
Wolfenbuttel's Avatar
 
Join Date: Jul 2006
Location: NY
Posts: 563
Images: 9
understandable but if u take a digital tester to check for power on a gfci it will trip.
Wolfenbuttel is offline   Reply With Quote
Reply

Bookmarks



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On

Sitemap:1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176
Sponsor Our Community

All times are GMT -5. The time now is 11:44 PM.


Powered by vBulletin® Version 3.7.0
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
Our lawyer tells us that, by pressing the "New Thread" or "New Reply" button, you acknowledge that the opinions and information expressed in your article are yours alone and not those of thereeftank.com, dba The Reef Tank. Further, you agree to indemnify The Reef Tank, its moderators, administrators and agents from any and all liability which may arise as a result of your article. (C)opyright 2006 TheReefTank.com